    Deep Sea 3110 Wiring Diagram Fault

    The Fault

    When the set is running at around 230V LN, the module appears to read just over 250V LN.

    The reason for the fault

    Deep Seas 3110 wiring diagram on the 3110 controller contains a wiring fault that has led to incorrect voltage readings showing on the screen on the DSE 3110 controller.

    On the diagram for the DSE 3110, it showed that the L1 should go into 8 on the back of the DSE and Neutral goes in to 9. This was later found to be incorrect. These two wires should be switched and this will correct the fault.

    Solution

    This can be corrected by switching the wiring on the reverse of the DSE using the following proceedure.

    1) Disconnect the battery, thereby isolating the set.
    2) Remove the plug that holds the DSE wires 8 and 9.
    3) Remove wire 104 (Neutral) and 153 (Live) and reconnect them so that 53 goes into number 9 on the DSE 3110 and 104 goes into 8 on the DSE.
    4) Reconnect the battery.
    5) Test the set again and it will now be showing the correct Voltage.
    Last edited by wellandpower; 08-18-2009 at 01:43 PM.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  2. Join Date
    Dec 2005
    Posts
    262

    Please see the correct module wiring diagram for the DSE 3110.
    Attached Files
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  3. Join Date
    Dec 2005
    Posts
    262

    Note that on Welland Sets using a 3110, a seperate voltmeter is used and while the 3110 reading is incorrect, the voltmeter reading will be correct.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

+ Reply to Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts