    Question Internal glazing and carbon buildup?

    Hello:
    Guys,is there anybody got what's the meaning of Internal glazing and carbon buildup?
    Cause my generator running at low speeds,low loads long time,search the google but could not understand it.

  2. #2
    Join Date
    Dec 2005
    Posts
    343

    Default

    Internal glazing of the engine is a problem caused by low load, as is carbon build up.
    You may also expereince this along with a symptom of oil leaking from the exhaust, turbo or manifold.

    When a diesel engine is under low load, the pressure in the cylinders falls. This causes a poor sealing of the piston ring, as it relys on the pressure. Low pressure in the cylinder can cause poor combustion and low cylinder tempuratures. Poor combustion leads to unburnt diesel and this clogs the piston rings, wich causes the sealing efficeiency to fall even more and makes the problem again worse.


    Glazing occurs when hot combustion gases blow past the poorly-sealing piston rings. This causes lubricating oil on the cylinder walls to 'flash burn', creating an hard glaze which smooths the bore and removes the "honing marks" machined into the bore surface which are there to hold oil and return it to the crankcase by the scraper piston ring.


    Does that help?
    How long has it been running for at low load?
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  3. #3
    Join Date
    Dec 2009
    Posts
    8

    Default

    absolutely it does,running for several months

  4. #4
    Join Date
    Dec 2005
    Posts
    343

    Default

    The best thing you can do it run it at standby rating and see if the unit improves.
    I would try and run it at full load for the whole day and see if it helps.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  5. #5
    Join Date
    Dec 2009
    Posts
    8

    Default

    Thanks,Charlie,i would let my assistant try it asap,although the genset should be run at low load for sometime

  6. #6
    Join Date
    Dec 2005
    Posts
    343

    Default

    What Engine do you have on your generator?
    Exactly what problems are you experiencing with it?
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  7. #7
    Join Date
    Dec 2009
    Posts
    8

    Default

    Back from Business Travel just now for almost a month,Farrow,thanks for your attention,my engine is Cummins with the alternator like stmaford,i guess the manufacturer copy from stamford.
    oil still leaking from exhaust ,and frame,sometimes ,it comes white gas,or black gas,with soot.
    May be i need purchase one more genset,the order are suck.

  8. #8
    Join Date
    Dec 2005
    Posts
    343

    Default

    What size of generator is it? Did you try and run it on full load? Did it not solve the problem?
    How old is it?

    Chinese generators often do not last like others I am afraid to say.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  9. #9
    Join Date
    Dec 2009
    Posts
    8

    Default

    yes,we solve the problem last month,tks for your attention,charlie