Thread: Unbalance Line current

  1. #1
    Join Date
    May 2010
    Posts
    9

    Default Unbalance Line current

    We have 5 gensets ran on parallel mode the load [50% each]were divided equally between 5 sets, but i observed 2 sets had unbalanced load current on L1,L2&L3[Line 1=380A;Line 2=280 & Line 3=360Amps] what is the probable cause.?

  2. #2
    Join Date
    Feb 2008
    Posts
    180

    Default

    Only 2 sets had unbalanced load? Are the voltages the same on each of the sets, even those with unbalanced load?

    Because if the balanced load between the 5 units, then if the current is different, then the voltages must be different also.

    If not, then the load is not balanced.

    Normally, poor load sharing is due to poor voltage control, poor engine control, a bad CT maybe?

  3. #3
    Join Date
    May 2010
    Posts
    9

    Default

    No Load output voltages between 5 sets is +/- 3% difference w/c is acceptable.
    On-Load voltage on parallel sets i can't tell the difference but i observed the power factor of line 2 w/ abnormal current is higher than L1&L3[L1=0.96;L2=0.99&L3=0.96]

    Thanks

  4. #4
    Join Date
    Dec 2005
    Posts
    343

    Default

    Is L2 different on all sets or just one set?
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  5. #5
    Join Date
    May 2010
    Posts
    9

    Default

    Just on 1 set..

  6. #6
    Join Date
    Dec 2005
    Posts
    343

    Default

    Seems a bit strange!
    Either poor control or a CT issue.

    Possibly a module issue?
    Try swapping the modules on 2 sets and seeing if the problem moved with the module or starys with the set.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

+ Reply to Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts