Thread: Differential Current Fault

  1. #1
    Join Date
    May 2010
    Posts
    9

    Default Differential Current Fault

    What is the possible cause/causes of intermittent Tripping of Differential Current Protection of Alternator.?
    I have this issue occassionally..

  2. #2
    Join Date
    Dec 2005
    Posts
    343

    Default

    The cause is likely to be a differential current fault! It provides rapid detection of generator Φ to Φ or Φ-G faults.

    How often is it happening? I assume the generator is big?
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  3. #3
    Join Date
    May 2010
    Posts
    9

    Default

    It's 1.2Mw 480v Alternator.
    I performed insulation test from phase to phase and phase to neutral.
    The readings were 1.2 megaohms from phase to G.>is this the possible cause?
    Ph to ph is still acceptable=10megaohms/volt.