    Default wiring diagram for a TAD941GE

    Guys,

    I have a generator with a TAD941GE shutting down shown a "CAN BUS ERROR" After a few run ins with Volvos, I know it's a loose or broken connection somewhere. Someone else was troubleshooting it before and pulled a real good number on the harness. Does anyone have a wiring diagram I can use to verify all connections at the engine? Thanks!

  2. #2
    Join Date
    Feb 2010
    Posts
    3

    Default Question 2

    What's the best way to test the ECM for power on this engine?

  3. #3
    Join Date
    Dec 2005
    Posts
    360

    Default

    If the engine is running at all, there is not a power issue.
    Without it the unit injectors will not function and hence it would not run.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

  4. #4
    Join Date
    Sep 2011
    Posts
    1

    Default

    Could any body send me the wiring schematics for TAD941GE Engine ?
    Is there any way to test this engine without CIU or DCU. ?

    Please help me in this issue

  5. #5
    Join Date
    Dec 2005
    Posts
    360

    Default

    You do need a DCU or CUI I am afraid to test this engine.

    We only use the 8 pin plug on these engines and they are wired as follows:

    Red - Fused Battery Positive
    Black - Battery Negative
    Green - ECU Stop
    Red / Blue - ECU Power

    The other wires are CAN. Most controllers use the J1939 pair to control the engine. If you use the wrong pair, or the wrong way round, it will not work.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator