    We have two problem on revived genset
    1. 225 kva- after run in two min engine goes to shutdown through "ECU shutdown " message. The engine is a TAD732GE.
    2. 695 kva - does not crank. Trying to attempt 6 times and goes to message "failure to start ". The engine is a TWD1643GE
    Pls advise us
    Thanks

  2. #2
    Join Date
    Dec 2005
    Posts
    360

    Default

    These units have all run before, so they should work.
    1) Does it display any warnings prior to shutdown?
    2) Check the CAN connection from the engine to the module.

    On the second one, you should perform this test:

    http://www.wellandpower.net/forums/s...310-Controller

    If it does not change the display to 0000 RPM from #### then your CANBUS connection has been disconnected, severed or is bad. Redoing this connection will correct the issue.

    On the small unit please check the coolant level and fill right to other top, even if you think it is full and let the engine expel any excess water. Low coolant level on Volvo engines sometimes causes some odd results.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

+ Reply to Thread

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts