Thread: Mecc Alte Alternator voltage not stable after changed to 60hz?

  1. #1
    Join Date
    Feb 2008
    Posts
    186

    Default Mecc Alte Alternator voltage not stable after changed to 60hz?

    Hi,

    I have just changed the speed of my generator to 60hz and now the frequency is not stable?
    What can I do?

  2. #2
    Join Date
    Dec 2005
    Posts
    360

    Default

    When you change from 50 to 60Hz, you need to set the stability pot on the AVR again.

    ** Caution, the AVR is live when the machine is running, only adjust it when the set is off. **

    Turn the STAB pot all he way anti-clockwise, then adjust it clockwise until the voltage becomes unstable.
    Then turn it back about 10 degrees.
    Charlie Farrow