Thread: Sets not syncing

  1. #1
    Join Date
    Mar 2006
    Posts
    22

    Default Sets not syncing

    Hi,

    I hope someone can help me, we have two sets that are supposed to be sync'ing and they are not. When the mains is thrown, only one set starts and the other set displays "MSC Error: Too Few Sets".

    I am using DSE 550 modules.

  2. #2
    Join Date
    Dec 2005
    Posts
    343

    Default

    Thank you for your question.

    This problem is caused when setting up a DSE 550 module for syncronising that has the incorrect number of sets set in the modules memory. When the number of sets is two small, for example it is set to 1, when there are two sets, the first set will start and the second will display the message "MSC Link: Too Few Sets".

    You should go into the P810 configuration software and read in the configuration from the controller and then goto:

    Re-Calibrate >> Sync + Load Control >> Multiset

    There is an option there called "Number Of Sets". In a two set system, this must be set to 2, on both controllers.

    When you have correct this, both sets should start.
    Charlie Farrow
    Sales Director
    http://www.wellandpower.net/
    All advice provided in these forums by us is for information only. Users of these forums should not rely on answers provided here. We accept no liability for use of this information. If you require professional advice, please contact sales for a rate.
    Perkins Generators - http://www.wellandpower.net/diesel_g...tors.generator
    Volvo Generators -
    http://www.wellandpower.net/diesel_g...ator.generator

+ Reply to Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts